Troubleshooting via Web UI Status Page

SecureSync’s Web UI includes pages that provide current “remote” status information about SecureSync. The following table includes information that can be used as a troubleshooting guidance if status fault indications or conditions occur.

Troubleshooting using the Web UI Status indications

Web UI Page location Current Status Indication Troubleshooting

HOME page, System Status panel, Status row

SYNC indicator is not “lit” (not Green).HOLD indicator is “lit” (Orange).—OR—FAULT indicator is “lit” (Red). Below the System Status panel there is an Out of Sync alarm statement SecureSync is in Holdover mode—OR—SecureSync is now out of Time Sync All available Input References have been lost. The Reference Status table on the HOME page will show the current status of all inputs (Green is valid and Red is invalid or not present).
1. Make sure the Input Reference Priority table still has the desired reference inputs Enabled, based on the desired priority. See Configuring Input Reference Priorities.
2. Make sure the desired input references are still connected to the correct input port of SecureSync.
3. Verify GNSS antenna installation (if applicable). See Troubleshooting GNSS Reception.

HOME page, System Status panel, Power row

AC and/or DC indicator is red instead of greenNOTE: The AC indicator will only display on the HOME screen if SecureSync is equipped with an AC power input. The DC indicator will only display on the HOME screen if SecureSync is equipped with a DC power input. Specified AC and/or DC input power is not present. Refer to Section Connecting Supply Power for AC and DC power connection information:
If AC indicator is red:
1. Verify AC power cord is connected to an AC outlet.
2. Verify AC power input switch is ON.
3. Check the two fuses in the AC power module.
If DC indicator is red:
1. Verify DC power source is within range specified at the DC power connector.
2. Verify DC power is present at the input connector.
3. Verify DC input polarity.

MANAGEMENT/ NTP Setup page

NTP Status Summary panel

Stratum row

Stratum 15 NTP is not synchronized to its available input references (SecureSync may have been in Holdover mode, but Holdover has since expired without the return of valid inputs) Note: If SecureSync was just recently powered-up or rebooted and input references are applied, no troubleshooting may be necessary. Allow at least 10-20 minutes for the input references to be declared valid and NTP to align to the System Time (allow an additional 35-40 minutes for a new install with GNSS input).
1. Verify in the Configure Reference Priorities table that all available references enabled. See Configuring Input Reference Priorities.
2. Verify that the Reference Status on the HOME page shows “OK” (Green) for all available references.
3. Verify NTP is enabled and configured correctly. See NTP Reference Configuration.

MANAGEMENT/ NETWORK page

Cannot login or access the Web UI. The following error message is displayed:
“Forbidden You don’t have permission to access/ on this server”
This message is displayed when any value has been added to the Network Access Rules table and your PC is not listed in the table as an Allow From IP address. To restore access to the Web UI, either
1. Login from a PC that is listed as an Allow From in this table; or
2. If it is unknown what PCs have been listed in the Access table, perform an unrestrict command to remove all entries from the Network Access Rules table. This will allow all PCs to be able to access the Web UI.